Most Recent Questions
Recent Question:
is there a way to get the propane gas amount in my cylinders on my iphone
Recent Question:
Genarator does not start when power is lost.
Recent Question:
hour meter shows more then it actualy has
Recent Question:
What are the three lights for on the outside panel
Recent Question:
Battery removal
Questions with Most Recent Answers
Question:
is there a way to get the propane gas amount in my cylinders on my iphone
Question:
Genarator does not start when power is lost.
Question:
hour meter shows more then it actualy has
Question:
What are the three lights for on the outside panel
Question:
Battery removal

Customer questions and answers for
Generac Power Systems 20kW-6730

Customer questions and answers:
482 Questions
 | 
536 Answers
Overall rating:
4.819 out of 5
4.8
out of
5

Customer questions and answers for Generac Power Systems 20kW-6730

Question

What does the 2(H) on the display panel mean?

State: LA - Louisiana
asked 6 months ago
Customer avatar
by
Robin
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The (H) reading on your unit’s control panel would allude to the amount of time that has passed since your unit was setup for automatic operation. Considering this, if your unit currently reads “2(H)”, this would insinuate that 2 hours have passed since your unit was installed and activated.
answered 6 months ago
Customer avatar
by
GeneracPowerSystems02
0points
0out of 0found this answer helpful.
Question

Can I use a 10w30 synthetic oil in a 20KW generator? I live in South Louisiana where the temps range from low 30's to 90's.

State: LA - Louisiana
Age: Over 65
asked 6 months ago
Customer avatar
by
Slick
South La.
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Per the unit’s owner’s manual, either a SAE30, 10W-30, or 5W-30 synthetic oil can be utilized on Generac’s Guardian Series automatic standby generators. Please note that our overarching recommendation for use after the unit’s break-in period, would be the 5W-30 synthetic oil, as it is manufactured for use in all temperature ranges. If you have any other product-related inquiries, please contact us directly at 888-GENERAC (436-3722).
answered 6 months ago
Customer avatar
by
GeneracPowerSystems02
0points
0out of 0found this answer helpful.
Question

Lattice screen around generator

Hi,
I have a Guardian whole house unit installed. Can I build a wooden lattice screen around the unit? The lattice has 1-inch holes in it. How far from the unit should the fence be positioned?
Thanks.
Jerry
State: PA - Pennsylvania
Age: Over 65
asked 6 months ago
Customer avatar
by
Jerry
Benton
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Our air-cooled units need to have 18 inches of clearance from the back, 3 ft on either side and in front, 5 ft above, and 5ft from any window, door or vent leading into the home. Moreover, we would recommend ensuring that you will not be restricting the flow of air to the unit, as it is an air cooled generator that requires proper ventilation; any damage due to lack of air provided to the unit is not covered under the product's warranty. Please note, however, that these recommendations are always superseded by local codes.
answered 6 months ago
Customer avatar
by
GeneracPowerSystems02
0points
0out of 0found this answer helpful.
Question

Just got a 20 kw generac, need to know the following

My 20 kw generac on the led board shows, missing charger AC. Should I be concerned. I don't have the wiring hooked up yet to the house. I have to get a certified electrican to have that done. I am thinking that message will go away once I have it wired up to my house. Let me know if I am on the right track.
State: PA - Pennsylvania
Age: 55-64
asked 6 months ago
Customer avatar
by
Prepper
Turbotville
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
If the T1 fuse in the transfer switch is blown, the T1 line provided at the generators control panel is not appropriately connected, or if the battery on the unit is low or dead, the “CHARGER MISSING AC” alarm will appear on the unit’s control panel. Considering that you have not hooked up the wiring to your unit at this time, this would likely be the cause of the current reading on your unit’s control panel. If issues persist after all of the wiring has been appropriately applied, we would recommend contacting an independent authorized service provider for diagnostic work. Please note that we would recommend removing the unit’s battery until wiring can be installed, as leaving it connected will cause the battery to drain and render the battery inoperable if/when it is prepared for use. To locate an independent authorized service provider closest to you, please use your postal code for searching purposes via the following link: http://www.generac.com/dealer-locat....
answered 6 months ago
Customer avatar
by
GeneracPowerSystems02
0points
0out of 0found this answer helpful.
Question

What is required for annual maintenance?

State: MO - Missouri
Age: Over 65
asked 7 months ago
Customer avatar
by
Frosty
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
All maintenance requirements are listed in the Maintenance section of the product’s owner’s manual. To locate this documentation online, please use the model or serial number of your product via the following link: http://www.generac.com/service-supp.... If you have any other product-related comments, questions, or concerns, please contact us directly at 888-GENERAC (436-3722).
answered 7 months ago
Customer avatar
by
GeneracPowerSystems02
0points
0out of 0found this answer helpful.
Question

Noise Reduction Options

I have a 6244 and its about a year old. We live in the city and its really loud. What are my options to deaden the sound?
State: FL - Florida
Age: 45-54
asked 7 months ago
Customer avatar
by
Dan2000
Tampa
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Generac designs our standby generators with sound attenuated panels and an aluminum, steel, or composite enclosure to minimize noise whenever possible. We make our best effort to manufacture our home standby generators to meet the noise level expectations of our customers. However, there are certain elements of operation that must be considered with an air-cooled engine driven product such as air flow requirements that limit our ability to further sound-proof the enclosure.

Also, please note that Generac’s 20kW automatic standby generator, model number 6730, features a noise rating of 66dB, at a distance of 23 feet, while operating at normal load. Also, when exercising the unit in Quiet-Test mode, the unit will exercise at 60dB, at a distance of 23 feet. Please know that we do not offer other accessories to allow for quieter operation, however, structural or decorative elements, such as a privacy fence, installed at an appropriate distance away from the unit may assist in reducing the noise experienced at a property line. The Guardian Series air cooled automatic standby generators require a minimum clearance of 36” from the ends (short sides) of the generator. However, the distance required from the unit to any window, vent, door, opening into the home, and trees, plants or shrubs over 12” in height is a minimum of 60”. If you have any other product-related inquiries, please contact us directly at 888-GENERAC (436-3722).
answered 7 months ago
Customer avatar
by
GeneracPowerSystems02
0points
0out of 0found this answer helpful.
Question

I have no keys for my generator cabinet

Model 0047260
Age: 45-54
asked 7 months ago
Customer avatar
by
LJ
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Please note that the keys are often zip-tied to the vents of your unit’s enclosure. However, if you do not have the keys in this location, we would recommend contacting us directly with your personal information, so that we can send them out to you as soon as possible. We can be reached at 888-GENERAC (436-3722).
answered 7 months ago
Customer avatar
by
GeneracPowerSystems02
0points
0out of 0found this answer helpful.
Question

The display reads "inspect battery". I did and it does not look like there is anything wrong with it. What should I do next ?

State: CT - Connecticut
Age: Over 65
asked 7 months ago
Customer avatar
by
Ben
Beacon Falls
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The “INSPECT BATTERY” alarm, and associated yellow LED light, allude to a maintenance reminder that will occur on an annual basis. To properly inspect the battery, we would recommend following the recommendations listed in your unit’s owner’s manual. To remove the side panel, merely unlock the unit’s hood, lift it up, and pull the front panel straight up. Once the panel is removed, the battery compartment should be revealed in the lower right hand corner of the unit’s enclosure. If your battery is not appropriately charged, we would recommend verifying that the T1 fuse, along with the T1 connections are appropriately applied in the generator and associated transfer switch. If the battery is dead, it would need to be replaced. If you have any other product-related inquiries, please contact us directly at 888-GENERAC (436-3722).
answered 7 months ago
Customer avatar
by
GeneracPowerSystems02
0points
0out of 0found this answer helpful.
Question

Green & yellow lights on.

My yellow & green light are both on. Info on the inside says battery inspection
The generator is 18mths old, turns over every Saturday morning without fail.
Do I need to replace the battery or do I need to do something else?

Ricky.
State: NJ - New Jersey
Age: 45-54
asked 7 months ago
Customer avatar
by
RickMarn
Morris Plains
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The “INSPECT BATTERY” alarm, and associated yellow LED light, allude to a maintenance reminder that will occur on an annual basis. To properly inspect the battery, we would recommend following the recommendations listed in your unit’s owner’s manual. To remove the side panel, merely unlock the unit’s hood, lift it up, and pull the front panel straight up. Once the panel is removed, the battery compartment should be revealed in the lower right hand corner of the unit’s enclosure. If your battery is not appropriately charged, we would recommend verifying that the T1 fuse, along with the T1 connections are appropriately applied in the generator and associated transfer switch. If the battery is dead, it would need to be replaced. If you have any other product-related inquiries, please contact us directly at 888-GENERAC (436-3722).
answered 7 months ago
Customer avatar
by
GeneracPowerSystems02
+1point
1out of 1found this answer helpful.
Question

How do I run test to ensure additional lights are powered by 20Kw generac generator during power outages?

State: LA - Louisiana
Age: 45-54
asked 8 months ago
Customer avatar
by
MrConcerned
New Orleans
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
2 answers
Answers
answer 1
I am under the impression that you want to see what the generator is capable of handling during a power outage? Other than what you were told.

Whole House Circuit Only

You may want to hire an electrician that has a amp clamp. turn on al your essential circuits and measure for 15 -20 min record in rush amps as well. As you add each additional light monitor amps. a safe load percentage According to NEC for your 20 kw is about 75% load capacity. 65 amps is a safe number. The rest can be used for surge and in rush amps.

Now if you want to know what is hooked up to your emergency panel . Simply turn all lights on and take notes what you have turned on .Kill service entrance breaker and review notes . Whatever is on after generator has took over is Emergency whatever stays off is non emergency . Wall plugs usually are on same breaker that your lights for each room are on .
I hope this helps
State: TX - Texas
Age: 35-44
answered 7 months ago
Customer avatar
by
Ferezco
Poteet
0points
0out of 0found this answer helpful.
answer 2
To test your automatic standby generator for functionality in the event of a utility outage, we would recommend staging such an outage, by setting the unit in the AUTO position, and disconnecting your home’s panel from a main utility feed. We would recommend having this task performed by an independent authorized dealer in your local area. To locate an independent authorized dealer closest to you, please use your postal code for searching purposes via the following link: http://www.generac.com/dealer-locat....
answered 7 months ago
Customer avatar
by
GeneracPowerSystems02
0points
0out of 0found this answer helpful.
Question

Whats is the tolerance for loss in water column pressure for a 300 kw generator?

asked 8 months ago
Customer avatar
by
J
Va
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
This question is answered based upon model of engine , liters , how many cylinders , and type of fuel and wether it's turbocharged or not.
State: TX - Texas
Age: 35-44
answered 8 months ago
Customer avatar
by
Ferezco
Poteet
0points
0out of 0found this answer helpful.
Question

Likely causes of propane smell

I have a 9.5 KW Guardian automatic standby generator. I smell propane when the generator is running. What is/are the likely causes/causes?
State: CA - California
Age: Over 65
asked 8 months ago
Customer avatar
by
Gary
Nevada City
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
2 answers
Answers
answer 1
First question
Have you always had that smell?
If so contact your nearest Generac Dealer .
It is very important that the Dealer verify proper set up and installation. Also to verify any leaks that the generator may have beyond the gas inlet source.
For your safety and of others it is expedient that this issue be resolved ASAP
State: TX - Texas
Age: 35-44
answered 7 months ago
Customer avatar
by
Ferezco
Poteet
+1point
1out of 1found this answer helpful.
answer 2
When installed appropriately, with the necessary configuration for supplying liquid propane fuel, the slight smell of propane is not uncommon. However, if you are concerned about the strength of the scent, we would recommend referring to your fuel line installer, to ensure that all connections were made appropriately, as a potential leak in the fuel line, or improper installation, could potentially be the cause of a stronger propane smell. Please note that the our automatic standby generators are manufactured for use with a natural gas fuel source out of the factory; the unit would need to be reconfigured for use with a liquid propane fuel source, per the recommendations listed in your unit’s owner’s manual.
answered 8 months ago
Customer avatar
by
GeneracPowerSystems02
+1point
1out of 1found this answer helpful.
Question

Is the wattage per mont/day/hour, etc?

Is the wattage per mont/day/hour, etc?

I am doing a science project for school Can you help me please?
State: NJ - New Jersey
Age: 18-24
asked 8 months ago
Customer avatar
by
sciencegeek
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The ratings provided for each unit’s wattage capabilities, are provided for continuous operation. When operating, Generac’s 20kw automatic standby generator, model number 6730, is rated for 20,000 watts on a liquid propane fuel source, and 18,000 watts on a natural gas fuel source. If you have any other product-related inquiries, please either refer to the unit’s owner’s manual (which can be accessed by utilizing the product’s model or serial number via the following link: http://www.generac.com/service-supp...), or contact us directly at 888-GENERAC (436-3722).
answered 8 months ago
Customer avatar
by
GeneracPowerSystems02
0points
0out of 0found this answer helpful.
Question

What should be on the digital screen after activation, "Ready to run and hours of protection"?

State: WV - West Virginia
Age: 25-34
asked 8 months ago
Customer avatar
by
Generac365
Huntington
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
2 answers
Answers
answer 1
That is correct. Unit will not work in auto function if unit has not been registered.
State: TX - Texas
Age: 35-44
answered 7 months ago
Customer avatar
by
Ferezco
Poteet
0points
0out of 0found this answer helpful.
answer 2
When Generac’s 20kw Guardian Series automatic standby generator, model number 6730, has been activated and prepared for operation, the control panel should in fact read, “Ready to Run” with a listing for the hours of protection since activation. If you have any other product-related inquiries, please contact us directly at 888-GENERAC (436-3722).
answered 8 months ago
Customer avatar
by
GeneracPowerSystems02
0points
0out of 0found this answer helpful.
Question

Stop Generator after extended time

I have a 20KW Guardian that is fueled by a 500gal propane tank. I would like to have the ability to disable the system after a certain run-time has elapsed (e.g. 2 days) to ensure that the generator does not drain the tank. Is there a method to turn the machine off automatically after an extended time?
Kirk
State: CO - Colorado
Age: 45-54
asked 8 months ago
Customer avatar
by
kirk
Durango
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
2 answers
Answers
answer 1
An easy way that this can be done is by having your propane company install a level sensor that can give you the ability to monitor fuel level and give you the ability to take action at different settings set at you discretion .for example when it reaches 25 % fuel it can send a message to supplier by email that you will need a fill up... Or you to allow you to take action..
State: TX - Texas
Age: 35-44
answered 7 months ago
Customer avatar
by
Ferezco
Poteet
+1point
1out of 1found this answer helpful.
answer 2
Generac brand automatic standby generators will perform as long as the unit is in the AUTO position, and utility power is absent; there is not a way to set up the system to be disabled after a specified period of time. Furthermore, we recommend stopping the unit after every 24 hours of continuous operation, for maintenance-related purposes described in the unit’s owner’s manual. Please note that any damage incurred to the unit when the unit is utilized for a period of time beyond these recommendations, or damage incurred due to a lack of proper maintenance is not covered under the product’s warranty. If you do not want the unit to run after a specified period of time, we would recommend turning the unit off via the unit’s control panel, and starting the unit back up once you would like to receive back-up power once again. If you have any other product-related inquiries, please contact us directly at 888-GENERAC (436-3722).
answered 8 months ago
Customer avatar
by
GeneracPowerSystems02
-1point
0out of 1found this answer helpful.
Question

20KW Guardian -- Detect Run and Disable Unnecessary Loads

I have a 20KW Guardian backing up full utility power to our mountain house. Fuel source is a propane tank. One of the loads on the system is a roof snow melt panel. During a power outage, I would like to disable the snow melt so that it doesn't unnecessarily drain the fuel on the generator. I need advice on how to do this with your system. I see two possibilities:
1) Detect a run indication from your system and use a relay to disable the snow melt. To date, I have been unable to locate a dry contact in either the transfer switch or the generator that indicates when the system running.
2) Use the "load shed" terminals in the transfer switch with a relay to disable loads. Unfortunately, from reading the manual, the load shed terminals do not disable loads, only turn them off temporarily when a "overload" occurs.
Can you advise on a good path forward?
Kirk
State: CO - Colorado
Age: 45-54
asked 8 months ago
Customer avatar
by
kirk
Durango
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
2 answers
Answers
answer 1
You can add an AC sensing relay. Hook it up at the lugs of the generator source lugs. Whenever you have generator source input . the relay energizes and can open or close a circuit . Depends on what you need to turn off your load. This will keep you from having to interfere into gen and ats circuitry
Hope this helps
State: TX - Texas
Age: 35-44
answered 7 months ago
Customer avatar
by
Ferezco
Poteet
0points
0out of 0found this answer helpful.
answer 2
If you are interested in locking out specific loads when the generator is operating, we would recommend considering the use of an Auxiliary Transfer Switch Contact Kit. This product allows the transfer switch installed with the generator to lock out a single large electrical load that you may not need during an utility power outage. Further information on this kit can be located online, by visiting the following link: http://www.generac.com/all-products.... To obtain this kit and have it properly installed, we would recommend working with an independent authorized dealer in your local area. To locate an independent authorized dealer in your local area, please use your postal code for searching purposes via the following link: http://www.generac.com/dealer-locat.... If you have any other comments, questions, or concerns, please contact us directly at 888-GENERAC (436-3722).
answered 8 months ago
Customer avatar
by
GeneracPowerSystems02
-1point
0out of 1found this answer helpful.
Question

On a 20KW automatic whole house generator, the 14-2 wire used as control and sensing can this wire be solid or strand or it doesn't matter.

State: MD - Maryland
Age: 55-64
asked 8 months ago
Customer avatar
by
DA
Annapolis
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
2 answers
Answers
answer 1
Depending on code. Stranded wire typically has a higher ampacity than solid. However, on the sensing circuit, this shouldn't matter that much unless the distance is extreme.
Kirk
State: CO - Colorado
Age: 45-54
answered 8 months ago
Customer avatar
by
kirk
Durango
0points
0out of 0found this answer helpful.
answer 2
While stranded wire should be utilized, we would recommend checking with your local inspector, to ensure that this requirement is acceptable within your local codes; local ordinances will always supersede our recommendations as the unit’s manufacturer. If you have any other product-related inquiries, please contact us directly at 888-GENERAC (436-3722).
answered 8 months ago
Customer avatar
by
GeneracPowerSystems02
+1point
1out of 1found this answer helpful.
Question

Proper transfer switch

I have two150AMP services to the meter coming into my home. I purchased a 20Kw Generic Generator for home back up. What is the correct transfer switch to use?
State: FL - Florida
Age: 55-64
asked 9 months ago
Customer avatar
by
Al
Home
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
2 answers
Answers
answer 1
You can use a 300 amp service entrance installed before both panels. Or use the 2 150 amp switches to match panels before each individual panel ether way will work . Generac offers both. Get a bid to install both ways to see what is more economical .
State: TX - Texas
Age: 35-44
answered 7 months ago
Customer avatar
by
Ferezco
Poteet
0points
0out of 0found this answer helpful.
answer 2
The automatic transfer switch that should be utilized in conjunction with your automatic standby generator depends upon your home’s configuration, main panel, and back-up power needs. In order to properly determine the specific transfer switch model most applicable for your personal set up and emergency power needs, we would recommend working with an independent authorized dealer in your local area. To locate an independent authorized dealer closest to you, please use your postal code for searching purposes here: http://www.generac.com/dealer-locat....
answered 9 months ago
Customer avatar
by
GeneracPowerSystems02
0points
0out of 0found this answer helpful.
Question

20kw NG pipe thru-put / distance from NG source

I want to put a Generac 20kw unit 70' from the NG utility source. I have a 1.25 or 1.50 inch supply line and the city NG flow is 275 CFH. I also have a gas range, hot water heater and furnaces. Will I have enough THRU-PUT for the 20kw unit at 70' (feet) ? If not, is there a smaller unit that would work? Thank you.
State: IL - Illinois
Age: 45-54
asked 9 months ago
Customer avatar
by
Ghram
Chicago
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
2 answers
Answers
answer 1
The most economical way would be to install a higher psi primary regulator . And then 2 individual secondary ; one for house and one for generator. Please refer to professional gas plumber to see if your meter has proper office to handle your needs.
State: TX - Texas
Age: 35-44
answered 7 months ago
Customer avatar
by
Ferezco
Poteet
0points
0out of 0found this answer helpful.
answer 2
Unfortunately, we are unable to size the appropriate unit for your back-up power needs via online correspondence. In order to properly determine the unit that will not only cover your needed power in the event of an utility outage, but also enable you to follow the specifications put in place by local codes, we would recommend working with an independent authorized dealer in your local area. Furthermore, we would recommend working with your local gas company, to ensure that your unit’s fuel source is appropriately configured for optimal use. To locate an independent authorized dealer closest to you, please use your postal code for searching purposes here: http://www.generac.com/dealer-locat....
answered 9 months ago
Customer avatar
by
GeneracPowerSystems02
0points
0out of 0found this answer helpful.
Question

Can the unit go with you after sale of house?

I'm currently renting, but will be purchasing a house within the next year or two. How easy and non destructive is being able to remove the unit and take it to the next residence?
State: CA - California
Age: 45-54
asked 9 months ago
Customer avatar
by
JonnieJJ
Camarillo
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
2 answers
Answers
answer 1
Best answer is to have it wired up with a generator inlet box . Allowing the customer to have the ability to use a portable and not having to change back any electrical changes that were made previously . Then when you get your house you can purchase an ats and set it up for standby.
State: TX - Texas
Age: 35-44
answered 7 months ago
Customer avatar
by
Ferezco
Poteet
0points
0out of 0found this answer helpful.
answer 2
While the unit can in fact be removed for transportation, any damage due to uninstallation and/reinstallation would not be covered. Furthermore, the generator’s warranty coverage is applied only to the original installation site. Once removed from that original installation site, the unit’s warranty will be voided. If you have any other product-related inquiries, please contact us directly at 888-GENERAC (436-3722).
answered 9 months ago
Customer avatar
by
GeneracPowerSystems02
0points
0out of 0found this answer helpful.