Search Generac

Looking for Answers about Generac Power Systems 20kW-6730?

Business Standby(Q:19 A:20)
Centurion Series(Q:201 A:225)
Commercial Series(Q:27 A:27)
EcoGen Series(Q:48 A:60)
GP Series(Q:757 A:887)
Guardian Series(Q:1139 A:1291)
Home Backup(Q:67 A:62)
LP Series(Q:136 A:133)
Parts & Accessories(Q:27 A:34)
Professional Grade(Q:11 A:10)
Protector Series(Q:21 A:22)
QuietSource Series(Q:84 A:83)
RS Series(Q:10 A:11)
Residential Grade(Q:175 A:206)
XG Series(Q:319 A:326)
XP Series(Q:191 A:203)
iX Series(Q:87 A:159)
Shop now at Generac
or
Choose a Category
Most Recent Questions
Recent Question:
Correct operaing manual?
Recent Question:
Why does my control panel say 123 hours of protection?
Recent Question:
Regarding 14KW Generac oil capacity...
Recent Question:
No lid key for Guardian series 20kW Generator
Recent Question:
How can the 1 phase generator be used with 3 phase house wiring
Questions with Most Recent Answers
Question:
Regarding 14KW Generac oil capacity...
Question:
Why does my control panel say 123 hours of protection?
Question:
Correct operaing manual?
Question:
No lid key for Guardian series 20kW Generator
Question:
How can the 1 phase generator be used with 3 phase house wiring

Customer questions and answers for
Generac Power Systems 20kW-6730

Customer questions and answers:
445 Questions
 | 
497 Answers
Overall rating:
4.889 out of 5
4.9
out of
5

Customer questions and answers for Generac Power Systems 20kW-6730

Question

Stop Generator after extended time

I have a 20KW Guardian that is fueled by a 500gal propane tank. I would like to have the ability to disable the system after a certain run-time has elapsed (e.g. 2 days) to ensure that the generator does not drain the tank. Is there a method to turn the machine off automatically after an extended time?
Kirk
State: CO - Colorado
Age: 45-54
asked 2 months, 3 weeks ago
Customer avatar
by
kirk
Durango
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
2 answers
Answers
answer 1
An easy way that this can be done is by having your propane company install a level sensor that can give you the ability to monitor fuel level and give you the ability to take action at different settings set at you discretion .for example when it reaches 25 % fuel it can send a message to supplier by email that you will need a fill up... Or you to allow you to take action..
State: TX - Texas
Age: 35-44
answered 1 month, 2 weeks ago
Customer avatar
by
Ferezco
Poteet
+1point
1out of 1found this answer helpful.
answer 2
Generac brand automatic standby generators will perform as long as the unit is in the AUTO position, and utility power is absent; there is not a way to set up the system to be disabled after a specified period of time. Furthermore, we recommend stopping the unit after every 24 hours of continuous operation, for maintenance-related purposes described in the unit’s owner’s manual. Please note that any damage incurred to the unit when the unit is utilized for a period of time beyond these recommendations, or damage incurred due to a lack of proper maintenance is not covered under the product’s warranty. If you do not want the unit to run after a specified period of time, we would recommend turning the unit off via the unit’s control panel, and starting the unit back up once you would like to receive back-up power once again. If you have any other product-related inquiries, please contact us directly at 888-GENERAC (436-3722).
answered 2 months, 3 weeks ago
Customer avatar
by
GeneracPowerSystems02
-1point
0out of 1found this answer helpful.
Question

What should be on the digital screen after activation, "Ready to run and hours of protection"?

State: WV - West Virginia
Age: 25-34
asked 2 months, 3 weeks ago
Customer avatar
by
Generac365
Huntington
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
2 answers
Answers
answer 1
That is correct. Unit will not work in auto function if unit has not been registered.
State: TX - Texas
Age: 35-44
answered 1 month, 3 weeks ago
Customer avatar
by
Ferezco
Poteet
0points
0out of 0found this answer helpful.
answer 2
When Generac’s 20kw Guardian Series automatic standby generator, model number 6730, has been activated and prepared for operation, the control panel should in fact read, “Ready to Run” with a listing for the hours of protection since activation. If you have any other product-related inquiries, please contact us directly at 888-GENERAC (436-3722).
answered 2 months, 3 weeks ago
Customer avatar
by
GeneracPowerSystems02
0points
0out of 0found this answer helpful.
Question

Likely causes of propane smell

I have a 9.5 KW Guardian automatic standby generator. I smell propane when the generator is running. What is/are the likely causes/causes?
State: CA - California
Age: Over 65
asked 2 months, 1 week ago
Customer avatar
by
Gary
Nevada City
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
2 answers
Answers
answer 1
First question
Have you always had that smell?
If so contact your nearest Generac Dealer .
It is very important that the Dealer verify proper set up and installation. Also to verify any leaks that the generator may have beyond the gas inlet source.
For your safety and of others it is expedient that this issue be resolved ASAP
State: TX - Texas
Age: 35-44
answered 1 month, 3 weeks ago
Customer avatar
by
Ferezco
Poteet
+1point
1out of 1found this answer helpful.
answer 2
When installed appropriately, with the necessary configuration for supplying liquid propane fuel, the slight smell of propane is not uncommon. However, if you are concerned about the strength of the scent, we would recommend referring to your fuel line installer, to ensure that all connections were made appropriately, as a potential leak in the fuel line, or improper installation, could potentially be the cause of a stronger propane smell. Please note that the our automatic standby generators are manufactured for use with a natural gas fuel source out of the factory; the unit would need to be reconfigured for use with a liquid propane fuel source, per the recommendations listed in your unit’s owner’s manual.
answered 2 months, 1 week ago
Customer avatar
by
GeneracPowerSystems02
+1point
1out of 1found this answer helpful.
Question

How do I run test to ensure additional lights are powered by 20Kw generac generator during power outages?

State: LA - Louisiana
Age: 45-54
asked 2 months ago
Customer avatar
by
MrConcerned
New Orleans
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
2 answers
Answers
answer 1
I am under the impression that you want to see what the generator is capable of handling during a power outage? Other than what you were told.

Whole House Circuit Only

You may want to hire an electrician that has a amp clamp. turn on al your essential circuits and measure for 15 -20 min record in rush amps as well. As you add each additional light monitor amps. a safe load percentage According to NEC for your 20 kw is about 75% load capacity. 65 amps is a safe number. The rest can be used for surge and in rush amps.

Now if you want to know what is hooked up to your emergency panel . Simply turn all lights on and take notes what you have turned on .Kill service entrance breaker and review notes . Whatever is on after generator has took over is Emergency whatever stays off is non emergency . Wall plugs usually are on same breaker that your lights for each room are on .
I hope this helps
State: TX - Texas
Age: 35-44
answered 1 month, 3 weeks ago
Customer avatar
by
Ferezco
Poteet
0points
0out of 0found this answer helpful.
answer 2
To test your automatic standby generator for functionality in the event of a utility outage, we would recommend staging such an outage, by setting the unit in the AUTO position, and disconnecting your home’s panel from a main utility feed. We would recommend having this task performed by an independent authorized dealer in your local area. To locate an independent authorized dealer closest to you, please use your postal code for searching purposes via the following link: http://www.generac.com/dealer-locat....
answered 2 months ago
Customer avatar
by
GeneracPowerSystems02
0points
0out of 0found this answer helpful.
Question

Keys to my 20KW don't open locks on my unit

The two keys that came with my 20KW Guardian Generac generator do not open the unit. Help!
State: FL - Florida
Age: 55-64
This product will backup: Entire Home
asked 3 years, 2 months ago
Customer avatar
by
CLHarris
Carrabelle
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Be sure to apply firm pressure to the lid of the generator when turning the key. If you need additional assistance, please contact 888-GENERAC.
State: WI - Wisconsin
answered 3 years, 2 months ago
Customer avatar
by
Generac
Waukesha
+3points
3out of 3found this answer helpful.
Question

How long can this generator run at a single time?

There's a hurricane coming, how long can this generator run if we lose power? The last time our area lost power after a significant storm, it was over a week before power was restored. Can our generator run this long (or longer)?
State: PA - Pennsylvania
Age: 35-44
This product will backup: Other
asked 3 years, 2 months ago
Customer avatar
by
JG
Glenmoore
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
We design standby generators specifically for extended run times, so having it run for a week or longer is definitely possible. Your only limitation is the fuel type, meaning the size of your propane tank or the supply of natural gas. For natural gas at ½ load, the 20kW uses 206 cubic feet per hour. For liquid propane at ½ load, the 20kW uses 1.89 gallons per hour. Refer to the 20kW spec sheet for additional fuel consumption data. http://www.generac.com/SpecSheets/0...

We also recommend stopping the unit and checking the oil after 24 hours of straight operation and performing scheduled maintenance after 200 hours of operation.
State: WI - Wisconsin
answered 3 years, 1 month ago
Customer avatar
by
Generac
Waukesha
+1point
1out of 1found this answer helpful.
Question

running gas line

My gas line and my circuit breaker box are at opposite ends of my house. I understand that without seeing the house, you can't tell me what is best for my house, but would you agree that in general it is more difficult, expensive and dangerous to run a natural gas line across a house than to run an electrical line across the house.
State: NY - New York
Age: 45-54
This product will backup: Entire Home
asked 3 years, 1 month ago
Customer avatar
by
Mike
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Typically it is more expensive and costly to run gas line since it needs to be trenched when compared to the electrical that can be run in the house. If it is a finished basement, then it really depends on the situation.

For more installation details, please refer to an authorized Generac dealer by using our dealer locator at: http://www.generac.com/Service/Deal...
State: WI - Wisconsin
answered 3 years, 1 month ago
Customer avatar
by
Generac
Waukesha
0points
0out of 0found this answer helpful.
Question

Connecting to an alarm panel

Hi - does this unit have a connection/contact to connect to an alarm panel. So alarm company can alert me if generator takes load?
State: CT - Connecticut
Age: 45-54
This product will backup: Entire Home
asked 3 years, 1 month ago
Customer avatar
by
Toniwhufc
Riverside
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
There is a set of dry contacts that are provided on the controller for connecting to an alarm in the event of unexpected shut down. Please refer to the owner's manual for location and specifics.

Manuals can be found on http://www.generac.com/Service/Manu...
State: WI - Wisconsin
answered 3 years, 1 month ago
Customer avatar
by
Generac
Waukesha
0points
0out of 0found this answer helpful.
Question

How do I turn off at night and back on in morning to preserve fuel?

I have a 20kw Guardian with an automatic transfer switch and would like to turn the unit off at night to save fuel. How do I do this?
State: CT - Connecticut
Age: 45-54
This product will backup: Entire Home
asked 3 years, 1 month ago
Customer avatar
by
Kevin
Reding
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
1. Turn the generator breaker off.
2. Switch the main electrical panel breaker to off.
3. Switch the three position switch to off.
4. Remove the fuse on the control panel. To put the generator back into service, simply follow the process in reverse.
State: WI - Wisconsin
answered 3 years, 1 month ago
Customer avatar
by
Generac
Waukesha
+1point
1out of 1found this answer helpful.
Question

Where is the serial number located on a Guardian 8 kW and 20kW?

I cannot find the metal data place anywhere. On the 8kW there is no data plate on the outside or inside. Help!
State: NY - New York
Age: 55-64
This product will backup: Entire Home
 
Products related to my question
 
 
asked 3 years, 1 month ago
Customer avatar
by
Goldfish
Delmar
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The data label is located inside of the generator near the control panel. For a diagram on where it's located on the 8kW and 20kW, please refer to page 6 on the owner's manual. This manual is shared between the 8kw - 20kW.

Manuals can be found on http://www.generac.com/Service/Manu... by entering in your seven-digit model number. Be sure to enter in your model number starting with two or three zeros without any dashes or spaces. For the 8kW, Model 5870-0 should be entered as 0058700.
State: WI - Wisconsin
answered 3 years, 1 month ago
Customer avatar
by
Generac
Waukesha
0points
0out of 0found this answer helpful.
Question

Is this the largest wattage that produces pure sine waves?

Is this the largest wattage that produces pure sine waves that runs on LP? After searching the other models by for the TruePower feature, this was the largest one I could find.
State: ME - Maine
This product will backup: Entire Home
asked 3 years, 1 month ago
Customer avatar
by
Josh
Maine
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
For air cooled automatic standby generators, the 20kW is the largest unit that features True Power Technology, which equals less than 5% total harmonic distortion.
State: WI - Wisconsin
answered 3 years, 1 month ago
Customer avatar
by
Generac
Waukesha
0points
0out of 0found this answer helpful.
Question

Wiring

In the installation guidelines in order to maintain seperation of circuits dc control wires must be seperated from the ac control wires with the fiberglass sleeve. Now do we also have to run the ac wires in one conduit and the dc in another ? or can we run both once it exits the generator
State: MI - Michigan
Age: 45-54
This product will backup: Entire Home
asked 3 years, 1 month ago
Customer avatar
by
John
Michigan
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Please consult with the local authority, as it may be required based on local code.

This is not an issue on the pre-wired EZ Switches, since it is factory installed wiring.
State: WI - Wisconsin
answered 3 years, 1 month ago
Customer avatar
by
Generac
Waukesha
-1point
0out of 1found this answer helpful.
Question

I have three 200 amp breaker panels but my overall consumption can be handled by a 20kw generator. What transfer switch(es) will I need?

asked 3 years, 1 month ago
Customer avatar
by
wayne
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Consult with authorized Generac Dealer for specific requirements. To find a dealer near you, use our dealer locator at: http://www.generac.com/Service/Deal...
State: WI - Wisconsin
answered 3 years, 1 month ago
Customer avatar
by
Generac
Waukesha
-4points
0out of 4found this answer helpful.
Question

20kw Generators

What is the difference between the generac 20KW generators model centurion 5896 and the guardian model 5875?
asked 3 years, 1 month ago
Customer avatar
by
generator ?
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The only difference between these models is the brand. The Centurion brand is manufactured exclusively for Lowes stores. Both are packaged with the same transfer switch and have the same product features.
answered 3 years, 1 month ago
Customer avatar
by
GeneracPowerSystems
+4points
4out of 4found this answer helpful.
Question

Noise reduction

Although the generator meets town's setbacks, my neighbor is complaining. Can anything be done to attenuate the noise?
State: NY - New York
Age: 45-54
This product will backup: Entire Home
asked 3 years, 1 month ago
Customer avatar
by
Ray
Bronxville
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Generac designs our standby generators with sound attenuated panels and an aluminum enclosure to minimize noise whenever possible. You can also set the day and time of the weekly exercise cycle. We do not offer other accessories to allow for quieter operation.
State: WI - Wisconsin
answered 3 years, 1 month ago
Customer avatar
by
Generac
Waukesha
0points
0out of 0found this answer helpful.
Question

Main Line Circuit Breaker

It is good to have protection for the generator, but it seems counter-intuitive to have the generator shut itself off if there is too much demand. This would be especially important if I am out of town and not in a position to turn off circuits and flip the switch to get the generator back on line.

I plan on getting a 20kW unit installed, which seems to be sized correctly for my house - and we would conserve power if in use. I would also shut down unessential circuits if going out of town. However, does the generator have the ability to restrict certain circuits so the demand does not overload the generator? Is there any control in the base model without accessories that provides this type of control?
State: RI - Rhode Island
Age: 45-54
This product will backup: Entire Home
asked 3 years, 1 month ago
Customer avatar
by
Dave
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
With Generac's Nexus Smart Switch, you can manage two 24V HVAC loads without any additional components. This will keep the generator from overloading. If you have other high-demand loads that could potentially overload the generator, you can add up to six additional digital load management (DLM) modules.
answered 3 years, 1 month ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

what is the input BTU for natural gas?

State: MA - Massachusetts
Age: Over 65
This product will backup: Entire Home
asked 3 years, 1 month ago
Customer avatar
by
sunshine
cape cod
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
294,000 BTU/hr is what would be needed to ensure a proper fuel supply at full load.
answered 3 years, 1 month ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

For LP hook-up, should the main line from the propane tank to the regulator be 3/4 inch pipe, or is 1/2 inch pipe sufficient?

Underground 250-gal propane tank is located 40 from where regulator enters house. Guardian 20kw to be installed near that regulator. Existing 40 ft buried main line from tank to regulator is 1/2 inch pipe. Is this sufficient to feed house and new generator, or should 1/2 pipe be replaced with a 3/4 inch pipe?
State: CT - Connecticut
This product will backup: Entire Home
asked 3 years, 1 month ago
Customer avatar
by
Greta
Northeast US
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
There are so many factors that can affect the gas pressure that we recommend an onsite inspection and professional recommendation by a LP gas professional. However, we are able to provide you with the fuel consumption rates and required water column which will help provide the correct size needed for installation. The required fuel pressure to the generator fuel inlet at all load ranges is 10 to 12 inches of water column for LP gas. Fuel consumption at full load is 2.9 gallons/hour. For additional information, please consult the spec sheet at http://www.generac.com/SpecSheets/0...
answered 3 years, 1 month ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

What size propane tank is required for a 20 KW generator?

asked 3 years, 1 month ago
Customer avatar
by
ken
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
For liquid propane at ½ load, the 20kW uses 1.89 gallons per hour. You can use this to size your LP fuel tank to accommodate the amount of running time you prefer. Refer to the 20kW spec sheet for additional fuel consumption data. http://www.generac.com/SpecSheets/0...
answered 3 years, 1 month ago
Customer avatar
by
GeneracPowerSystems
+5points
5out of 5found this answer helpful.
Question

What size wire do I use between Generac RTS-D200A3 transfer switch to a Generac 20kw generator?

State: CT - Connecticut
Age: 45-54
This product will backup: Entire Home
asked 3 years, 1 month ago
Customer avatar
by
Sparky
Monroe
on 20kW-6730
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Typically a #4 wire is used, but it may have to be a heavier gauge depending upon the distance between the generator and the transfer switch. We recommend consulting a Generac dealer for more information. You can find a dealer near you by visiting http://www.generac.com/Service/Deal...
answered 3 years, 1 month ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.