Most Recent Questions
Recent Question:
Extreme Snow Conditions - Snorkling
Recent Question:
I have two main breaker panels, and the circuits are spread across both.
Recent Question:
How do I convert from natural gas to liquid propane?
Recent Question:
Max Size of Main AC Wire for Model 6244
Questions with Most Recent Answers
Question:
How do I convert from natural gas to liquid propane?
Question:
What are the overall dimensions of the Guardian 8kw unit?
Question:
How much propane will the 20kw unit burn if it runs full tilt for one week?
Question:
What yearly maintenance procedures does this unit require?

Customer questions and answers for
Generac Power Systems 20kW Guardian Series Automatic Standby Generator A

20kw
Customer questions and answers:
338 Questions
 | 
372 Answers
Overall rating:
4.877 out of 5
4.9
out of
5

Customer questions and answers for Generac Power Systems 20kW Guardian Series Automatic Standby Generator A

Question

use of menu-hours used

I read manual. How do you tell how many hours used. Manual not clear on exactly how to access menu to do different functions
I would like step by step use of menu. Manual is too general for me.
State: NJ - New Jersey
Age: Over 65
This product will backup: Entire Home
asked 3 months, 4 weeks ago
Customer avatar
by
Happy
West Long Branch
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The 20kW Guardian Series automatic standby generator has an hour meter that can be viewed on the generator’s control panel. To determine the hours of run time on the unit, you will navigate the control panel to the Status Menu, select the Display option, and choose Engine Hours. This will show the total run time of the engine in hours. Please see the attached menu map for assistance. The menu map is also located in the owner’s manual for the unit. To locate a copy of the owner’s manual, search the model or serial number for your unit here: http://www.generac.com/Service/Manu....
User submitted photo
answered 3 months, 4 weeks ago
Customer avatar
by
GeneracPowerSystems01
0points
0out of 0found this answer helpful.
Question

If I change oil and filter myself does it void my warranty?

For my new 20kw Guardian, if I follow all break in times and oil recomendations in my owner's manual, and use Generac brand oil and filter, does changing the oil and filter myself void my warranty?

Specifically, do all oil and filter changes have to be done by a Generac dealer to maintain warranty coverage? (Unit was installed by Generac certified dealer)
State: CT - Connecticut
Age: 55-64
This product will backup: Entire Home
 
Products related to my question
 
asked 4 months ago
Customer avatar
by
tombrown5
Stonington
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Maintenance on the automatic standby generator is not required to be performed by a certified servicing dealer. The owner’s manual provided with the unit will include maintenance steps for items such as changing the oil, but if you are unfamiliar or uncomfortable with the required maintenance, our certified servicing dealers are able to provide service for the generators. Performing the maintenance on your own unit would not void the factory warranty unless the unit becomes damaged due to improper servicing. Please ensure that any and all maintenance performed is fully documented, as proof of maintaining the unit may be required for warranty claim purposes.
answered 4 months ago
Customer avatar
by
GeneracPowerSystems01
+1point
1out of 1found this answer helpful.
Question

What oil is used from factory ? Kind and weight.

Oil weight and type would depend on the weather which can change during the year. Oil change can go 2 years.
This product will backup: Entire Home
 
Products related to my question
 
asked 4 months, 1 week ago
Customer avatar
by
rosslink
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The 20kW automatic standby generator is shipped from factory with SAE 30 non-synthetic oil. Please see the attached chart for other oil weight recommendations.
User submitted photo
answered 4 months ago
Customer avatar
by
GeneracPowerSystems01
0points
0out of 0found this answer helpful.
Question

208/230 3 phase AC system

Can the 20k unit power an 208/230 3 phase AC system rated at 110 LRA (natural gas system)
State: NJ - New Jersey
Age: 55-64
This product will backup: Entire Home
asked 4 months, 1 week ago
Customer avatar
by
Fazzman
Freehold
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The 20kW automatic standby generator is a single phase unit, and is not compatible with a three phase system. If a three phase generator is required, we recommend considering our QuietSource series units.
We recommend contacting a Generac certified dealer for assistance in determining the proper generator and switch necessary for your application. To locate a certified dealer, search your postal code here: http://www.generac.com/Service/Deal....
answered 4 months ago
Customer avatar
by
GeneracPowerSystems01
0points
0out of 0found this answer helpful.
Question

which oil grade is best for my 20kw

I live in Central Texas close to Fort Worth are and our temps range from the low teens to 110, which grade of oil is the best for this temperature range? Or is there a grade of sythetic oil that is best for this region?
State: TX - Texas
asked 4 months, 1 week ago
Customer avatar
by
J.T.
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
For our automatic standby generators, if you expect the temperature to drop below freezing, we recommend utilizing a 5W-30 Synthetic oil. Synthetic is a good oil to use if you are looking for a general year-round oil for areas that have significant season changes.
answered 4 months, 1 week ago
Customer avatar
by
GeneracPowerSystems01
+2points
2out of 2found this answer helpful.
Question

For a 20kw unit my manual says nothing about changing the oil after 8 hrs. No break in period is mentioned at all. Where exactly would that be located

Or should I assume I can change the oil once a year or 200 hundred hours. thanks
State: MA - Massachusetts
This product will backup: Entire Home
asked 4 months, 1 week ago
Customer avatar
by
tc
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Our current production models do not list the 8 hour break in period as the new engines no longer require a break in. This eliminates the need for the 8 hour oil change, and will allow the oil to be changed immediately to a different weight for operation in colder temperatures. We recommend checking the Service Schedule in the owner’s manual to determine if your generator is exempt from the 8 hour oil change. To locate a copy of the owner’s manual, search the model or serial number for your generator here: http://www.generac.com/Service/Manu....
answered 4 months, 1 week ago
Customer avatar
by
GeneracPowerSystems01
+1point
1out of 1found this answer helpful.
Question

Weight on Gas Connection Mounting Hole

In the process of installing the 20kW Guardian. Yesterday the propane company completed the final installation. What I see is 3/4" black pipe (6" length) threaded onto the generator's gas supply mounting hole. The installer also added a regulator and cleanout (the latter also made of black pipe). All of this connects to a flexible connector (theirs, not the one Generac supplied with the generator) and finally to the flexible underground gas pipe. In all there are four 6" lenghts of black pipe, 3 - 90 degree elbows (black pipe), and a regulator hanging off the gas supply hole. There is no other support provided. Does this create a weight/torque problem when the generator is running (i.e., can the generator support this)?
State: MA - Massachusetts
Age: 55-64
This product will backup: Entire Home
asked 4 months, 1 week ago
Customer avatar
by
MikeNY07
Northborough
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The fuel line connection point on the generator is not designed to bear the full weight of the rigid fuel lines and regulator. We would recommend contacting your fuel line installer to ensure that the rigid line is properly supported to prevent damage to the generator.
answered 4 months, 1 week ago
Customer avatar
by
GeneracPowerSystems01
0points
0out of 0found this answer helpful.
Question

how do you ajust test runs to once a month?

It is a 20000 kw unit.
State: VA - Virginia
Age: 45-54
This product will backup: Entire Home
asked 4 months, 1 week ago
Customer avatar
by
big M
GLOUCESTER
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The unit is programmed to exercise weekly for 12 minutes; there is no option to change the length of time between exercise cycles.
answered 4 months, 1 week ago
Customer avatar
by
GeneracPowerSystems01
+1point
1out of 1found this answer helpful.
Question

What is the correct LRA rating for the 20k model?

I have spoken to several certified dealers in my NJ area. I get conflicting information on what is the maximum LRA rating for the 20k (natural gas) model. One guy says its is rated for 145 LRA. The other guy says 112. Both are registered dealers, installers and certified repair techs. The 112 guy claims based on his experience AC systems drawing more than 112 LRA have actually experienced damage because there was insufficient kickoff amps despite the ratings for 145. So I am both confused and concerned since I will need to upgrade my AC unit and need to know what AC unit will work with this 20k machine BEFORE I go into this project. ie. What LRA max rating is completely safe for the new 5 ton AC that I will need to install?
State: NJ - New Jersey
Age: 55-64
This product will backup: Entire Home
asked 4 months, 2 weeks ago
Customer avatar
by
Fazzman
Freehold
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
A 20kW when running on propane can handle a maximum locked rotor amp (LRA) rating of approximately 145; we do not have a listed rating for operation on natural gas. The capability of the generator will decrease when operating on natural gas. Please keep in mind that this rating is the maximum for the unit, and other appliances and loads that will be on the generator need to be taken into consideration as well. We recommend speaking to your local Generac certified dealer or certified electrician to determine the proper size generator necessary for your application. To locate a certified dealer, search your postal code here: http://www.generac.com/Service/Deal....
answered 4 months, 2 weeks ago
Customer avatar
by
GeneracPowerSystems01
0points
0out of 0found this answer helpful.
Question

do the 17 20 kw generators come set up for lp or natural

State: NY - New York
Age: 55-64
asked 4 months, 2 weeks ago
Customer avatar
by
harry425
long island
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Our home standby generators up to 48kw come set from the factory for natural gas but are easily field convertible to propane. To convert from natural gas to propane, and vice versa, you will want to reference the section in the owner’s manual titled “Reconfiguring the Fuel System.”
answered 4 months, 2 weeks ago
Customer avatar
by
GeneracPowerSystems01
0points
0out of 0found this answer helpful.
Question

can this unit be installed indoors with proper ventalation?

asked 4 months, 2 weeks ago
Customer avatar
by
Dean
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
These units are an outdoor installation only, and should therefore not be installed in any enclosed area.
answered 4 months, 2 weeks ago
Customer avatar
by
GeneracPowerSystems01
+1point
1out of 1found this answer helpful.
Question

Can unit be placed inside shop and exhausted outside.

Temp. drops to 40 below. Want unit inside so it will start with no problem.
Age: 55-64
This product will backup: Entire Home
asked 4 months, 2 weeks ago
Customer avatar
by
Bus
Saskatchewan
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
These units are an outdoor installation only, and should therefore not be installed in any enclosed area.
For our automatic standby generators, if you expect the temperature to drop below freezing, we recommend utilizing a 5W-30 Synthetic oil, which can be used year round. We also recommend using a cold weather kit, which includes a battery warmer and a crankcase heater. Using the correct oil and cold weather kit will allow the generator to start and run in below freezing temperatures.
answered 4 months, 2 weeks ago
Customer avatar
by
GeneracPowerSystems01
0points
0out of 0found this answer helpful.
Question

Unbolting the pad from the 20KW generator

I see where you mentioned unbolting the pad from the generator so you can use those holes to then bolt the generator and pad down to your concrete pad. How is that pad bolted to the generator? Do you have to somehow left the generator up to get to nuts underneath the pad? Thanks!
State: OH - Ohio
Age: 45-54
This product will backup: Entire Home
asked 4 months, 2 weeks ago
Customer avatar
by
Eddie
Central Ohio
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The automatic standby units can be mounted to a concrete pad using the 1 3/16 ” diameter bolt holes in the interior of the enclosure. When the unit is delivered, there will be bolts already occupying those spaces, as that is how the composite mounting pad is connected to the base of the generator. You would remove the existing bolts in order to properly anchor the generator and composite mounting pad to your concrete pad. The bolts would be removed from the underside of the generator before placing it on the concrete slab, as they feed from the bottom, up. A diagram of the hole locations is included in your owner’s manual under the Installation Diagrams section. The bolt diameter should equal that of the existing bolts, and should be a height of approximately three inches; however, the distance as to which the bolts are sunk into the concrete would be determined either by your local inspector if mounting is required by local code, or by your installer to ensure that the unit is properly anchored.
answered 4 months, 2 weeks ago
Customer avatar
by
GeneracPowerSystems01
0points
0out of 0found this answer helpful.
Question

Is there a calculation chart for sound output as you move away from the generator?

Model005887-1
State: NY - New York
Age: 35-44
This product will backup: Entire Home
asked 4 months, 3 weeks ago
Customer avatar
by
Joanie
Garden City
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The decibel ratings for our automatic standby generators are taken at a distance of 23 feet. Typically you will see a decrease in decibel levels the further away you are from the unit, but this is dependent on surrounding structures and environments. Due to the variable surroundings, we cannot accurately determine what the sound levels will be at other distances.
answered 4 months, 3 weeks ago
Customer avatar
by
GeneracPowerSystems01
0points
0out of 0found this answer helpful.
Question

what is the decibel output for the 20k Guardian unit

State: NY - New York
Age: Over 65
This product will backup: Entire Home
asked 4 months, 3 weeks ago
Customer avatar
by
fisherman
oakdale
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The 20kW automatic standby generator has a decibel rating of 66, at a distance of 23 feet while operating at normal load.
answered 4 months, 3 weeks ago
Customer avatar
by
GeneracPowerSystems01
+1point
1out of 1found this answer helpful.
Question

Can I install both a 5928 and 5951 remote monitors on my 20KW system?

I recently acquired a Generac Guardian 20KW (005875-1) whole house backup system. It is working well. I've also installed the cold weather kit and a model 5928 remote monitor.

The instruction manual for the Basic Nexus Remote Monitor says that you can add a second remote display by simply pairing it with the first display's transceiver. While I am not planning to do this right away, I am curious how I can obtain a second remote display unit without buying a complete kit. Is there a spare part number that provides just the basic remote display? Is it the 0H8075 part number that's in the instruction manual? If so, what's the price?

Is the transceiver for the 5928 basic remote monitor compatible with the display unit for the 5951 advanced remote display? Or vice-versa? I've read the owner's manual for the 5951 and it clearly has a different interface to the controller electronics. If I were to decide to get the 5951 at some point in the future, will I be able to continue to use the remote display from my 5928? Is it possible to have both units installed in a single generator system? (I would imagine that I'd need to do a customer modification of the enclosure to provide a way to mount the second transceiver from the 5951 if the two displays can not be paired to a single transceiver, and I would not be surprised if the two have incompatible signalling, given how they obtain data from the controller module).

Some feedback on the 5928 kit: The mounting screws are really TINY and it's really hard to attach the transceiver housing without losing at least one of the screws (with its TINY washer) down inside the generator housing. I lost one of the screws that way. There are only two screws in the kit (with two washers). That's silly. You should have at least three screws and washers, and ideally they would be a size you can readily buy at Home Depot or Lowes, not something you might be lucky to find (after you read the parts list) at a really good local hardware store (my local True Value franchise stocks things like the 3mm x 12 machine screws and the 3mm washers, I got lucky). A more reasonable choice would be something that's small and self-tapping and readily available from many sources, with more than two of them in the kit.
State: NH - New Hampshire
Age: Over 65
This product will backup: Entire Home
asked 4 months, 3 weeks ago
Customer avatar
by
DrTom
Amherst
on 20kW Guardian Series Automatic Standby Generator A
+1point
1out of 1found this question helpful.
Answer this question
1 answer
Answers
answer 1
The automatic standby generator, when paired with the Basic Nexus Wireless Remote Monitor, is able to support a second display monitor. This second display monitor can be ordered through your local certified dealer. Pricing and availability would be provided to you by the certified dealer. To locate a certified dealer, search your postal code here: http://www.generac.com/Service/Deal....
When the generator is paired with the Advanced Nexus Wireless Remote Monitor, it is only able to support one single display monitor. The generator is not able to utilize both the Basic and the Advanced Nexus Wireless Remote Monitors at the same time, as they do not utilize the same transceiver.
We also thank you for your feedback regarding the installation of the wireless remote monitor. Your comments and suggestions have been forwarded to the appropriate persons.
answered 4 months, 3 weeks ago
Customer avatar
by
GeneracPowerSystems01
+1point
1out of 1found this answer helpful.
Question

how close to your house can it be

State: LA - Louisiana
Age: 35-44
This product will backup: Entire Home
asked 4 months, 4 weeks ago
Customer avatar
by
Eric Bourgeois
New Orleans
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
2 answers
Answers
answer 1
exhaust needs to be 48" from any window or door opening..That's the township enforcement code where I live.
State: NJ - New Jersey
Age: 45-54
This product will backup: Entire Home
answered 4 months, 3 weeks ago
Customer avatar
by
stevek
Galloway
0points
0out of 0found this answer helpful.
answer 2
The Guardian Series automatic standby generators feature a one hour fire rated enclosure, and are in compliance with NFPA 37 Article 4.1.4 Condition 2 for clearance from combustible construction. Please see the attached installation diagram which includes clearance information. Further information on proper installation can be found in the installation guidelines. A copy of the installation guidelines can be located by searching the model or serial number for the generator here: http://www.generac.com/Service/Manu.... We recommend contacting your local inspector, as state and local codes may vary, and will supersede manufacturer recommendations for installation near a structure.
User submitted photo
answered 4 months, 3 weeks ago
Customer avatar
by
GeneracPowerSystems01
0points
0out of 0found this answer helpful.
Question

Where can I find the Company instruction on the distance from my house for installing my 20,000 watt Model 5875?

State: NJ - New Jersey
Age: Over 65
This product will backup: Entire Home
asked 5 months ago
Customer avatar
by
Bruce
Montclair
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The Guardian Series automatic standby generators feature a one hour fire rated enclosure, and is in compliance with NFPA 37 Article 4.1.4 Condition 2 for clearance from combustible construction. Please see the attached installation diagram which includes clearance information. Further information on proper installation can be found in the installation guidelines. A copy of the installation guidelines can be located by searching the model or serial number for the generator here: http://www.generac.com/Service/Manu....
User submitted photo
answered 5 months ago
Customer avatar
by
GeneracPowerSystems01
0points
0out of 0found this answer helpful.
Question

Over load protection

I have 400A service to this house. Would like to install a 20KW generator for some back up service when power goes out. Can get your 400A transfer switch but the instant load to the 20KW may cause an over load before I can cut off some breakers. Will the generator breaker act fast enough to protect the generator from damage?
State: LA - Louisiana
Age: Over 65
This product will backup: Entire Home
asked 5 months ago
Customer avatar
by
ED
Hammond
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The 20kW unit can cover a wide range of household appliances and items, however the exact items it can cover will vary for each application. The 20kW automatic standby generator is rated for a continuous output of 20,000 watts when utilizing propane, with a rated amperage of 83.3 amps at 240 volts. When utilizing natural gas, the unit is rated for a continuous output of 18,000 watts, with a rated amperage of 75 amps at 240 volts. You will want to ensure that all of the items you intend to run will not exceed this rating.
The breaker on the generator is designed only as accidental overload protection. If you are concerned that the loads you will be applying to the unit will immediately overload the generator, the generator may be too small for your application. To prevent this, the generator can be installed in many different configurations, including configurations where multiple transfer switches can be utilized, or sub-panels can be protected, provided the installation meets all local, state, and national codes. We recommend contacting your local certified sales dealer for sizing assistance. To locate a certified sales dealer, search your postal code here: http://www.generac.com/Service/Deal....
answered 5 months ago
Customer avatar
by
GeneracPowerSystems01
+1point
1out of 1found this answer helpful.
Question

What causes "RPM sense loss" warning code?

Have 20KW Vtwin on LP. Set to operate on Auto. Has been doing auto exersise once per week on regular bases. Last week it did not automatically initiate exersise . I tried to manually start the unit to test engine operation. It cranked a few seconds but did not start and stopped cranking. The control panel displayed "RPM sense loss" and I could do nothing to clear that. What are the likely problems for me to look at. I am an electrical engineer with lots of technical skills so I can handle technical guidence. I have checked the LP tank and there is fuel and the battery is fully charged.Thanks for your help.
State: IL - Illinois
Age: Over 65
This product will backup: Entire Home
asked 5 months ago
Customer avatar
by
Electricnemra
Goreville
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
During cranking, if the Control Board does not see a valid RPM signal within three (3) seconds, it will shut down and lock out on RPM sense loss. While the engine is running, if RPM signal is lost for one (1) second the Control Board will shut the engine down, wait 15 seconds, then re-crank the engine. If no RPM signal is detected within the first three (3) seconds of cranking, the Control Board will shut the engine down and latch out on RPM sense loss. If the RPM signal is detected, the engine will start and run normally. If the RPM signal is subsequently lost again, the Control Board will try one more re-crank attempt before latching out and displaying the RPM sense failure message.
If this alarm continuously appears when you attempt to start the unit, we would recommend contacting a Generac certified service technician. To find one in your area, search your postal code here: http://www.generac.com/Service/Deal....
answered 5 months ago
Customer avatar
by
GeneracPowerSystems01
0points
0out of 0found this answer helpful.