Recent Question:
How many B.T.U's does 20kw pull, with natural gas?
Recent Question:
Why isn't there any way to remotely start and stop the generator?
Recent Question:
Surge capability for starting certain motors
Questions with Most Recent Answers
Question:
How many B.T.U's does 20kw pull, with natural gas?
Question:
Can I run an 8kw standby generator on a 100 lb propane tank?
Question:
does a 120 liter tank fit generacs 14kv?
Question:
How many hours does the generator last if it has a 100 pound propane gas tank
Question:
How long will the unit run @50% load on 1, 100 gal. propane tank?

Customer questions and answers for
Generac Power Systems 20kW Guardian Series Automatic Standby Generator A

Customer questions and answers:
323 Questions
 | 
350 Answers
Overall rating:
4.876 out of 5
4.9
out of
5

Customer questions and answers for Generac Power Systems 20kW Guardian Series Automatic Standby Generator A

Question

Can the life expectancy of this generator be extended past 3000 hours with replacement parts?

The answer to a previous question was "With proper maintenance, it could last up to 3000 hours".
Could the life expectancy of the generator be extended with replacement parts?
Thank you.
State: NY - New York
Age: 45-54
This product will backup: Entire Home
 
Products related to my question
 
asked 1 year, 7 months ago
Customer avatar
by
Emma
Stone Ridge
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The "3000 hour" mark is not an absolute--only a milestone. The generator can run for a very long time with proper maintenance, and some individual components can be replaced to extend the life of the unit.
answered 1 year, 7 months ago
Customer avatar
by
GeneracPowerSystems
+1point
1out of 1found this answer helpful.
Question

does this generator come with a pre-wired flex conduit like the 10 kw?

State: NJ - New Jersey
Age: 35-44
This product will backup: Entire Home
asked 1 year, 7 months ago
Customer avatar
by
Aj
Wyckoff
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
No, this unit does not. The pre-wired conduit is part of Generac's EZ Switch, which can be purchased separately for use with this unit.
answered 1 year, 6 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

what size propane tank should i use for the 20kw Guardian series ?

State: NY - New York
Age: 55-64
This product will backup: Entire Home
asked 1 year, 7 months ago
Customer avatar
by
book of james
Northeast
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
That really depends upon how long you would like it to run during a power outage. To help you determine the answer to that question, we can provide you with fuel consumption rates for this unit. For LP fuel, the 20kW Guardian Series consumes 1.89 gal/hr at 1/2 load and 2.90 gal/hr at full load. You can use these data to determine how much fuel you want to have on hand to run your backup generator.
answered 1 year, 7 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

Could you tell me how many inches in from the back right corner the electrical knockout and the propane line hookup are for the 20kW gardian?

I am going to pour an over-sized concrete pad and want to know where to leave a hole in this pad to be able to run both the electrical and gas lines.
State: VT - Vermont
Age: 45-54
This product will backup: Entire Home
asked 1 year, 7 months ago
Customer avatar
by
Peter
Dummerston
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Please see the owner's manual at http://goo.gl/y8XpH. Beginning on page 33 you will find a number of installation drawings that will give you the dimensions you need.
answered 1 year, 6 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

Can this unit be modified to run on gasoline

asked 1 year, 7 months ago
Customer avatar
by
Rick
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
No. If you would like a portable gasoline-powered generator of comparable size, we recommend Generac's GP175000E--one of the largest on the market.
 
Products related to my answer
 
answered 1 year, 6 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

If the Guardian Series 20kW generator is installed on pea gravel, how often does it need to be re-leveled?

I have a Guardian Series 20kW residential generator that is mounted on pea gravel. As the generator runs during the weekly tests, it seems to settle and is no longer level (by approximately 2 inches). Will I need to continue to re-level the generator to keep within the 0.5 inch recommendation found in the manual?
State: IL - Illinois
Age: 25-34
This product will backup: Entire Home
asked 1 year, 7 months ago
Customer avatar
by
jgalamb2
Chicago
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
If the site is tamped down it should only need to be leveled once. If you are in an area where the ground is softer or absorbs more water than normal, it could be more often.
answered 1 year, 6 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

Air Conditioner Surge

My understanding is that the 20kw model has a surge rating of 145 amps at a 30% voltage dip. If the Lock Rotor Amp rating on my 5-ton central air conditioner is 140, does that imply that the generator should be able to start the unit without a problem?
State: NY - New York
Age: 45-54
This product will backup: Entire Home
asked 1 year, 7 months ago
Customer avatar
by
Rich
Long Island
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The generator's power output is affected by the fuel the system is using, the ambient temperatures during use, and elevation above sea level. To be sure that this model will power your central air conditioner, we recommend discussing with a licensed electrician or a Generac dealer (http://www.generac.com/Service/Deal...).
answered 1 year, 6 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

Dimensions of Guardian series 20 kW

What is the "foot print" of the Guardian 20 kW with the fascia? Need to make sure the pad I am preparing is big enough to allow for the generator and fascia.
State: IN - Indiana
Age: 55-64
This product will backup: Entire Home
asked 1 year, 6 months ago
Customer avatar
by
Chuckster
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The dimensions (L" x W" x H") of this unit are 48 x 25 x 29. Generac recommends that a concrete base slab should exceed the length and width of the generator by a minimum of six (6) inches (0.152 meters) on all sides; this should easily accommodate the fascia.
answered 1 year, 5 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

How do I turn the exercise time off?

asked 1 year, 6 months ago
Customer avatar
by
SKC
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
You cannot turn the exercise cycle off. It is required for the generator to exercise once a week for 10 - 15 minutes to ensure that it will function properly during a power outage. You do have the ability to schedule when this occurs at any time of day or night, but it cannot be disabled.
answered 1 year, 6 months ago
Customer avatar
by
GeneracPowerSystems
+1point
1out of 1found this answer helpful.
Question

Wire feeds

Is the wire feed from the generator to the transfer switch through the bottom of the case, or is it strictly through the back of the case? There was nothing in the installation guide specifically addressing this.
State: MD - Maryland
This product will backup: Entire Home
asked 1 year, 6 months ago
Customer avatar
by
Jenz
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
If this is referring to where the wire enters the transfer switch, there are knock outs on the bottom right and left side but a hole can be punched elsewhere if you want to have the wires enter from another location.
answered 1 year, 6 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

which base (concrete vs. just gravel) is better to install the generator?

asked 1 year, 6 months ago
Customer avatar
by
jack
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Both are acceptable, but one might be required over the other by your local building code authorities. We recommend discussing your local code requirements with them before making a decision.
answered 1 year, 6 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

20kw modle, is LP intake designed for Liquid LP or Gas State LP

State: SD - South Dakota
Age: 45-54
This product will backup: Entire Home
asked 1 year, 6 months ago
Customer avatar
by
Mark
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
It is designed for LP vapor (gaseous state).
answered 1 year, 6 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

FOT THE 20KW GUARDIAN IS IT BEST TO USE 5W40 EVEN IN THE SUMMER?

ALSO, SHOULD I CHANGE OIL AND FILTER AFTER INITIAL 8 HRS OF USE?
asked 1 year, 6 months ago
Customer avatar
by
AJ
UNION COUNTY, NJ
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Regarding oil, Generac recommends that all oil meet minimum American Petroleum Institute (API) Service Class SJ, SL or better. Use no special additives. The appropriate viscosity oil grade should be used according to the following operating temperature ranges.

• SAE 30: Above 32° F
• 10W-30: Between 40° F and -10° F
• Synthetic 5W-30: 10° F and below

We do recommend you change the oil and filter after first eight (8) hours of operation and then every 200 hours thereafter, or 2 years, whichever occurs first. You should change it sooner when operating under a heavy load or in a dusty or dirty environment or in high ambient temperatures.
User submitted photo
answered 1 year, 5 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

20 kw generator producing 240v single phase ..in terms of household current.

20 kw 240v single phase = 83 amps (approx)
What is the maximum househould (120v) amperage this unit can supply?
State: NJ - New Jersey
Age: 55-64
This product will backup: Entire Home
asked 1 year, 6 months ago
Customer avatar
by
steve
Bergen
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The rated maximum continuous load current at 240V AC is 83.3 amps when running on liquid propane fuel and 75 amps on natural gas fuel. For additional information, please see the spec sheet at http://www.generac.com/SpecSheets/0...
answered 1 year, 6 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

WHAT IS DECIBEL NOISE LEVEL AND AT WHAT DISTANCE FOR 20KW GUARDIAN

State: NJ - New Jersey
Age: 45-54
This product will backup: Entire Home
asked 1 year, 6 months ago
Customer avatar
by
JOE
MONROEVILLE
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
At 23 ft. with the generator operating at normal load, the unit produces 66 dB(A). At the same distance in Quiet-Test low-speed exercise mode, the unit produces 60 dB(A).
answered 1 year, 6 months ago
Customer avatar
by
GeneracPowerSystems
+2points
2out of 2found this answer helpful.
Question

Can I mount my 20KW generator on a trailer/dolly so that it can be "portable"?

I have a very narrow side yard and need to be able to store the generator in my garage and just wheel it our during the "bad seasons" when my power goes out. I can hanle the disconnects for gas and power. Is there any reason for not mounting it on a utility trailer and then using appropriate jacks to level it when I need it.
Thanks.
State: NJ - New Jersey
Age: 55-64
This product will backup: Entire Home
 
Products related to my question
 
asked 1 year, 6 months ago
Customer avatar
by
Tony
NJ
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The 20kW Guardian Series is not intended to be used in this way. Please consider installing it permanently. If your building codes will allow it, the unit can be installed as close as 18" to your home. This might make permanent installation an option in your situation. Otherwise, we would recommend a GP17500 portable generator instead, in conjunction with a manual transfer switch.
 
Products related to my answer
 
answered 1 year, 6 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

what is the set back from buildings on the Guardian 20KW? where can I find this info?

State: MA - Massachusetts
Age: 55-64
This product will backup: Entire Home
asked 1 year, 6 months ago
Customer avatar
by
Mark R
Weston
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
If your local building codes will allow it, you can install this unit as close as 18" to your home, with a minimum of 5' of clearance on either side. For specific information about how close you can install your generator to the home, please see the owner's manual at http://goo.gl/vodrK. Be sure to consult with your local code authority to make sure that our recommendations comply with local codes.
answered 1 year, 6 months ago
Customer avatar
by
GeneracPowerSystems
+1point
1out of 1found this answer helpful.
Question

Just tried to order this unit at home deopot, it's out of stock, when will it be available?

State: NH - New Hampshire
Age: 35-44
This product will backup: Entire Home
asked 1 year, 6 months ago
Customer avatar
by
Rick
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
I am passing your question on to our partners at The Home Depot; they will answer your directly via e-mail.
answered 1 year, 6 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

Concrete Pad Mounting -- Does Unit Have to Be Anchored?

I poured a concrete pad in anticipation of a purchase, although local code doesn't require it. The 20KW unit has arrived, but has not been placed on the pad yet. Can the unit with the composite mounting pad just sit on the concrete pad without being anchored, or do I need to install anchor bolts?
 
Products related to my question
 
asked 1 year, 6 months ago
Customer avatar
by
George
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
If your local code doesn't require a concrete pad, then it doesn't likely require that a generator installed on concrete pad be anchored to the pad. As long as your local code authority finds it acceptable, this is not a problem.
answered 1 year, 6 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

Do the AC/DC control wires need to be separated for local code reasons (if required) or for proper operation of the unit?

State: IL - Illinois
Age: 45-54
This product will backup: Entire Home
asked 1 year, 6 months ago
Customer avatar
by
Eric
Schaumburg
on 20kW Guardian Series Automatic Standby Generator A
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The separation is required by the National Electric Code.
answered 1 year, 5 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.