Search Generac

Looking for Answers about Generac Power Systems 20kW Whole House Switch?

Business Standby(Q:16 A:16)
Centurion Series(Q:210 A:229)
Diesel Generators(Q:12 A:13)
EcoGen Series(Q:39 A:49)
GP Series(Q:703 A:814)
Gaseous Generators(Q:46 A:44)
Guardian Series(Q:970 A:1079)
Home Backup(Q:61 A:56)
LP Series(Q:126 A:121)
Parts & Accessories(Q:17 A:23)
Protector Series(Q:31 A:31)
QuietSource Series(Q:35 A:36)
Residential Grade(Q:126 A:138)
XG Series(Q:295 A:297)
XP Series(Q:181 A:190)
iX Series(Q:82 A:146)
Shop now at Generac
or
Choose a Category
Most Recent Questions
Recent Question:
what comes whith it and how much is installation
Recent Question:
Model #6439: how much LPG does it consume per hour?
Recent Question:
What is need to install a permenant system?
Questions with Most Recent Answers
Question:
what comes whith it and how much is installation
Question:
Model #6439: how much LPG does it consume per hour?
Question:
What is need to install a permenant system?

Customer questions and answers for
Generac Power Systems 20kW Whole House Switch

Customer questions and answers:
399 Questions
 | 
430 Answers
Overall rating:
4.882 out of 5
4.9
out of
5

Customer questions and answers for Generac Power Systems 20kW Whole House Switch

Question

Noise reduction

Although the generator meets town's setbacks, my neighbor is complaining. Can anything be done to attenuate the noise?
State: NY - New York
Age: 45-54
This product will backup: Entire Home
asked 2 years, 7 months ago
Customer avatar
by
Ray
Bronxville
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Generac designs our standby generators with sound attenuated panels and an aluminum enclosure to minimize noise whenever possible. You can also set the day and time of the weekly exercise cycle. We do not offer other accessories to allow for quieter operation.
State: WI - Wisconsin
answered 2 years, 7 months ago
Customer avatar
by
Generac
Waukesha
0points
0out of 0found this answer helpful.
Question

Main Line Circuit Breaker

It is good to have protection for the generator, but it seems counter-intuitive to have the generator shut itself off if there is too much demand. This would be especially important if I am out of town and not in a position to turn off circuits and flip the switch to get the generator back on line.

I plan on getting a 20kW unit installed, which seems to be sized correctly for my house - and we would conserve power if in use. I would also shut down unessential circuits if going out of town. However, does the generator have the ability to restrict certain circuits so the demand does not overload the generator? Is there any control in the base model without accessories that provides this type of control?
State: RI - Rhode Island
Age: 45-54
This product will backup: Entire Home
asked 2 years, 7 months ago
Customer avatar
by
Dave
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
With Generac's Nexus Smart Switch, you can manage two 24V HVAC loads without any additional components. This will keep the generator from overloading. If you have other high-demand loads that could potentially overload the generator, you can add up to six additional digital load management (DLM) modules.
answered 2 years, 7 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

what is the input BTU for natural gas?

State: MA - Massachusetts
Age: Over 65
This product will backup: Entire Home
asked 2 years, 7 months ago
Customer avatar
by
sunshine
cape cod
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
294,000 BTU/hr is what would be needed to ensure a proper fuel supply at full load.
answered 2 years, 7 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

For LP hook-up, should the main line from the propane tank to the regulator be 3/4 inch pipe, or is 1/2 inch pipe sufficient?

Underground 250-gal propane tank is located 40 from where regulator enters house. Guardian 20kw to be installed near that regulator. Existing 40 ft buried main line from tank to regulator is 1/2 inch pipe. Is this sufficient to feed house and new generator, or should 1/2 pipe be replaced with a 3/4 inch pipe?
State: CT - Connecticut
This product will backup: Entire Home
asked 2 years, 7 months ago
Customer avatar
by
Greta
Northeast US
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
There are so many factors that can affect the gas pressure that we recommend an onsite inspection and professional recommendation by a LP gas professional. However, we are able to provide you with the fuel consumption rates and required water column which will help provide the correct size needed for installation. The required fuel pressure to the generator fuel inlet at all load ranges is 10 to 12 inches of water column for LP gas. Fuel consumption at full load is 2.9 gallons/hour. For additional information, please consult the spec sheet at http://www.generac.com/SpecSheets/0...
answered 2 years, 7 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

What size propane tank is required for a 20 KW generator?

asked 2 years, 7 months ago
Customer avatar
by
ken
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
For liquid propane at ½ load, the 20kW uses 1.89 gallons per hour. You can use this to size your LP fuel tank to accommodate the amount of running time you prefer. Refer to the 20kW spec sheet for additional fuel consumption data. http://www.generac.com/SpecSheets/0...
answered 2 years, 7 months ago
Customer avatar
by
GeneracPowerSystems
+5points
5out of 5found this answer helpful.
Question

What size wire do I use between Generac RTS-D200A3 transfer switch to a Generac 20kw generator?

State: CT - Connecticut
Age: 45-54
This product will backup: Entire Home
asked 2 years, 7 months ago
Customer avatar
by
Sparky
Monroe
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Typically a #4 wire is used, but it may have to be a heavier gauge depending upon the distance between the generator and the transfer switch. We recommend consulting a Generac dealer for more information. You can find a dealer near you by visiting http://www.generac.com/Service/Deal...
answered 2 years, 7 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

How much peak power will it provide for starting motors and air conditioners?

State: NY - New York
Age: 55-64
This product will backup: Entire Home
asked 2 years, 7 months ago
Customer avatar
by
Bill
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
145 amps at a 30% voltage dip.
answered 2 years, 7 months ago
Customer avatar
by
GeneracPowerSystems
+1point
1out of 1found this answer helpful.
Question

Set Up and Programming

I am considering installing a 20KW generator in my home and my dealer says that I need to have them program and start up my unit which they want to charge me a lot of money to do. Is this something that either my electrician or I can handle?

Thank you.
State: NJ - New Jersey
Age: 55-64
This product will backup: Refrigerator Freezer
asked 2 years, 6 months ago
Customer avatar
by
Builder
New Jersey
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
There is an activation that needs to be done, but it can be done by a homeowner. However, a 20kW will require the electrician since they will need to pull the meter face for transfer switch installation.
answered 2 years, 6 months ago
Customer avatar
by
GeneracPowerSystems
-1point
0out of 1found this answer helpful.
Question

Will this gen set start in colder climates -20 or even colder

QT20 aircooled I have a lady that would like this gen set, but is worried that it will not start in cold weather -10 or colder.Unit will be outside.Can this unit sit inside if operating on proprane?
State: MT - Montana
Age: 45-54
This product will backup: Entire Home
asked 2 years, 6 months ago
Customer avatar
by
Mr Wire
Wolf Point
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
It will work as long as a cold weather kit is installed and synthetic oil is used. For information about the appropriate viscosity oil to use, see the owner's manual at http://goo.gl/UF991
answered 2 years, 6 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

Fuel consumption and power output

I see on the spec sheet the natual gas requirement to run the generator at half load and at full load. Does the generator only run at those two speeds or does it run at variable speeds depending on the amount of power needed? For example, if my power went out and the only items in my house running required only 1kw to power them, what speed would the generator run at? Full load, half load, or something less than that?
State: IL - Illinois
Age: 45-54
This product will backup: Entire Home
asked 2 years, 6 months ago
Customer avatar
by
Doug
Deerfield
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The generator operates at a constant 3600 RPM, but will consume more fuel as more load is added. The full load and half load fuel consumption information is included as a benchmark. If your system is loaded at less than 50%, then your generator will use something less than the amount of fuel consumed at half load.
answered 2 years, 6 months ago
Customer avatar
by
GeneracPowerSystems
-3points
0out of 3found this answer helpful.
Question

surge current

what is the surge current or surge KW for the 20KW generator? For whaqt duration?
State: NJ - New Jersey
Age: Over 65
This product will backup: Entire Home
asked 2 years, 6 months ago
Customer avatar
by
prudent
Millstone township
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Surge wattage is generally 150% of the rated wattage, and lasts about 3 seconds.
answered 2 years, 6 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

will the exercise cycle work if the generator has run the day before on a new install

asked 2 years, 6 months ago
Customer avatar
by
al
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Yes. The exercise can be programmed to run at any time.
answered 2 years, 6 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

Can the life expectancy of this generator be extended past 3000 hours with replacement parts?

The answer to a previous question was "With proper maintenance, it could last up to 3000 hours".
Could the life expectancy of the generator be extended with replacement parts?
Thank you.
State: NY - New York
Age: 45-54
This product will backup: Entire Home
 
Products related to my question
 
asked 2 years, 6 months ago
Customer avatar
by
Emma
Stone Ridge
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The "3000 hour" mark is not an absolute--only a milestone. The generator can run for a very long time with proper maintenance, and some individual components can be replaced to extend the life of the unit.
answered 2 years, 6 months ago
Customer avatar
by
GeneracPowerSystems
+1point
1out of 1found this answer helpful.
Question

does this generator come with a pre-wired flex conduit like the 10 kw?

State: NJ - New Jersey
Age: 35-44
This product will backup: Entire Home
asked 2 years, 6 months ago
Customer avatar
by
Aj
Wyckoff
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
No, this unit does not. The pre-wired conduit is part of Generac's EZ Switch, which can be purchased separately for use with this unit.
answered 2 years, 5 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

Could you tell me how many inches in from the back right corner the electrical knockout and the propane line hookup are for the 20kW gardian?

I am going to pour an over-sized concrete pad and want to know where to leave a hole in this pad to be able to run both the electrical and gas lines.
State: VT - Vermont
Age: 45-54
This product will backup: Entire Home
asked 2 years, 6 months ago
Customer avatar
by
Peter
Dummerston
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
Please see the owner's manual at http://goo.gl/y8XpH. Beginning on page 33 you will find a number of installation drawings that will give you the dimensions you need.
answered 2 years, 5 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

Can this unit be modified to run on gasoline

asked 2 years, 6 months ago
Customer avatar
by
Rick
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
No. If you would like a portable gasoline-powered generator of comparable size, we recommend Generac's GP175000E--one of the largest on the market.
 
Products related to my answer
 
 
 
answered 2 years, 5 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

If the Guardian Series 20kW generator is installed on pea gravel, how often does it need to be re-leveled?

I have a Guardian Series 20kW residential generator that is mounted on pea gravel. As the generator runs during the weekly tests, it seems to settle and is no longer level (by approximately 2 inches). Will I need to continue to re-level the generator to keep within the 0.5 inch recommendation found in the manual?
State: IL - Illinois
Age: 25-34
This product will backup: Entire Home
asked 2 years, 5 months ago
Customer avatar
by
jgalamb2
Chicago
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
If the site is tamped down it should only need to be leveled once. If you are in an area where the ground is softer or absorbs more water than normal, it could be more often.
answered 2 years, 5 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

Air Conditioner Surge

My understanding is that the 20kw model has a surge rating of 145 amps at a 30% voltage dip. If the Lock Rotor Amp rating on my 5-ton central air conditioner is 140, does that imply that the generator should be able to start the unit without a problem?
State: NY - New York
Age: 45-54
This product will backup: Entire Home
asked 2 years, 5 months ago
Customer avatar
by
Rich
Long Island
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The generator's power output is affected by the fuel the system is using, the ambient temperatures during use, and elevation above sea level. To be sure that this model will power your central air conditioner, we recommend discussing with a licensed electrician or a Generac dealer (http://www.generac.com/Service/Deal...).
answered 2 years, 5 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

Dimensions of Guardian series 20 kW

What is the "foot print" of the Guardian 20 kW with the fascia? Need to make sure the pad I am preparing is big enough to allow for the generator and fascia.
State: IN - Indiana
Age: 55-64
This product will backup: Entire Home
asked 2 years, 5 months ago
Customer avatar
by
Chuckster
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
The dimensions (L" x W" x H") of this unit are 48 x 25 x 29. Generac recommends that a concrete base slab should exceed the length and width of the generator by a minimum of six (6) inches (0.152 meters) on all sides; this should easily accommodate the fascia.
answered 2 years, 4 months ago
Customer avatar
by
GeneracPowerSystems
0points
0out of 0found this answer helpful.
Question

How do I turn the exercise time off?

asked 2 years, 5 months ago
Customer avatar
by
SKC
on 20kW Whole House Switch
0points
0out of 0found this question helpful.
Answer this question
1 answer
Answers
answer 1
You cannot turn the exercise cycle off. It is required for the generator to exercise once a week for 10 - 15 minutes to ensure that it will function properly during a power outage. You do have the ability to schedule when this occurs at any time of day or night, but it cannot be disabled.
answered 2 years, 5 months ago
Customer avatar
by
GeneracPowerSystems
+1point
1out of 1found this answer helpful.